Hello I have been following the instructions for the sample project below. Right now I am stuck though on TCONN error 8602. Connecting a S7-1200 / S7-1500 to a SQL Database Am I missing something? TIA17 |
5/2/2022 9:44 PM | |
Joined: 8/3/2021 Last visit: 10/17/2023 Posts: 25 Rating: (2) |
Please let us know if you figure this out because I am having same issue. |
5/3/2022 7:59 AM | |
Joined: 4/25/2017 Last visit: 4/4/2024 Posts: 424 Rating: (66) |
Hi, You got a test error... Substatus is 80A4. I checked your screenshots. The remote IP address is wrong. The online values are for your PLC-IP. Offline the Server address is written. Load the offline values and try again.
|
Best Regards, |
|
This contribution was helpful to1 thankful Users |
4/11/2024 1:59 PM | |
Joined: 1/18/2023 Last visit: 5/2/2024 Posts: 3 Rating: (0) |
Just wanted to add a reply to this conversation in case anyone finds it useful. We were experiencing an issue with TCON returning 16#80CE and attached is a document showing what we found and how we resolved it. Basically the HWID was incorrect in the configuration but it was missing from the source project once we upgraded it. Regards AttachmentLSQL config problem explanation.pdf (9 Downloads) |