Hi, I am not sure about opening new topic, similar issue happened to me. In the system all servo motors losses their posiiton since alarm1980 PN: interruption cyclic connection. I checked telegram communication is 105 and the system includes unmanaged switches. I will try to change it with managed switch and my question is should I need any changes for device configuration in the plc program after replacing switch? Thank you, ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/03/2024 08:45:41New subject after splitting |
|
5/3/2024 1:31 PM | |
Joined: 7/7/2010 Last visit: 11/8/2024 Posts: 15388 Rating: (2443) |
The link to the split thread has the answer - unmanaged switch. Are you not able to "daisy-chain" the PN connections between devices? You know, out of the PLC, into S210, out of S210 on to other drive(s), and so on, and then out of PLC on other PN port to HMI - or unmanaged switch. For IRT, unmanaged switches are going to present problems - even the best of them. They have no clue what to do with deterministic PN packets (IRT/ISO) and will mess up the PN packet timing.
|
science guy |
|
5/3/2024 2:43 PM | |
Joined: 1/8/2024 Last visit: 10/15/2024 Posts: 32 Rating: (0) |
I will make a small correction, the system has S120 drives. I totally understand what do you mean but the system has other instruments with profinet connection. So, I am not sure if it is applicable as your defining. At least I am planning the change switch with managed ones.
|