I suggest two other options with less overhead and stress of get/put on your 410 if the skid is very large, assuming supervisory control from PCS7 AS is not required and you just want the skids on the HMI screens: 1. Direct manual integration of the 1500 into WinCC via S7-1200/1500 driver OMS+ or even classic S7 TCP/IP if you are not using optimized DBs. Just add the driver under tag management and configure tags and alarms and graphics like you would in WinCC without PCS7. Of course, these are not part of the PCS7 config and you have to do it all manually. 2. Use the additional package PCS7 OPEN OS (or perhaps even OPEN OS with MTP if you are lucky to have an MTP package unit) to integrate into PCS7 natively through DBA. OPEN OS allows the creation of block icons that can be completely APL analogous to give same look and feel. Caveat for using OMS+ is your (PCS7) WinCC version needs to be new enough, hopefully you aren't on legacy version. If you are, suggest you do your version upgrade to provide support for this integration. |