Has anyone successfully solved this problem? I've been trying to integrate a new Zone, as we call it, in our PCS7 system, and while the hardware is all recognized, configured, and accepted, when it goes to compile it complains loudly about being unable to detect any hardware at the given address on the PV_Outs. PV_In on the AI modules seems to work fine..I can read sensors, but no analog outputs are working. The values get all the way through the chart right into the Pcs7AnOu block, then vanishes. Nothing goes on the PV_Out. No explanation given. It simply refuses to find the hardware at QW688, and insists that it's looking at AW688 instead in the error message. It makes me believe that the block itself is diverting the connection on purpose. I'm near losing my mind... IM is an ET200MP with backplane AO module is an 6ES7 532-8TF00-0AB0 ------------------------------------------------------------------------------------------ |
Last edited by: Moderator_Lan at: 08/30/2024 07:10:52New subject after splitting |
|
8/30/2024 5:09 AM | |
Joined: 3/14/2008 Last visit: 10/8/2024 Posts: 2109 Rating: (941)
|
Hi, You should check out the Released Modules manual. In there you can find all components released for PCS7. The ET 200MP is not listed, so it may not work or you will not get all functionality like automatic driver connections and such. If it's not supported, you can try to set the Mode manually. Normally the attached signal is detected and the proper Mode is set by the system like 4-20mA, 0-20mA, 0-10V etc otherwise a Bad signal occurs. If you press F1 on the driver block Pcs7AnIn for example, you get info about the proper mode. For analog inputs 4-20mA (most often used) it's 16#80000203. If setting the mode is not working, there may be a another problem. Getting help is then not so easy since the module is not released for PCS7.
|
If I could help you, you can use the RATE button. Thank you. |
|
Follow us on