(0)| 12/19/2024 2:06 PM | |
|
Joined: 5/12/2006 Last visit: 1/16/2026 Posts: 22804 Rating:
|
remove the protection in V19 open/Upgrade after that to V20 set protection again in v20 |
| 12/19/2024 2:11 PM | |
|
Joined: 6/13/2017 Last visit: 9/26/2025 Posts: 25 Rating:
|
is this the only solution? because I have already modified some code... |
| 12/19/2024 2:12 PM | |
|
Joined: 5/12/2006 Last visit: 1/16/2026 Posts: 22804 Rating:
|
yes is the only one |
This contribution was helpful to
|
|
| 12/19/2024 2:13 PM | |
|
Joined: 6/13/2017 Last visit: 9/26/2025 Posts: 25 Rating:
|
sad.. ok thanks I will do it so Thanks ;) |
| 12/19/2024 2:28 PM | |
|
Joined: 7/9/2015 Last visit: 1/15/2026 Posts: 4496 Rating:
|
Hi, it´s a system behaviour and you can read this in manual of V20: Upgrading know-how protected blocks Regards, Towome |
|
|
|
| 12/21/2024 10:21 AM | |
|
Joined: 4/28/2015 Last visit: 12/4/2025 Posts: 42 Rating:
|
Hi, since TIA Portal V14 the KnowHowProtection can be also removed after the upgrade to a newer TIA Portal Version. 1. Edit the corresponding library type, e.g. via Mass operation by selecting a group in the program blocks folder. 2. Remove the Know-Protection, e.g. as mass operation in Overview or using TIA Add-ins like "Step7EngineeringAssistant" or "KnowHowProtect" 3. Set the KnowHowProtection again. 4. Release the types Regards Matthias |
Last edited by: Matthias.Co at: 12/21/2024 10:23:18Last edited by: Matthias.Co at: 12/21/2024 10:23:30Last edited by: Matthias.Co at: 12/28/2024 14:06:57 |
|