Hello, if there's no way to retrieve the current password, the only solution is resetting to factory settings. If activated, the XML-Interface can be used. You could use the demo tool: https://support.industry.siemens.com/cs/ww/en/view/109824195 Probably the final option would be Chapter 10.3 “Factory settings” in the manual page 135. You'll have to build a custom cable to do this. https://support.industry.siemens.com/cs/ww/en/view/109989409 |
| 10/6/2025 7:20 AM | |
|
Joined: 1/7/2025 Last visit: 11/5/2025 Posts: 16 Rating:
|
Hello, there's no harm in resetting to factory settings. As long as I can find the WBM password. 1. XML-Interface: I tried this, but it didn't work. I can't connect and get an error. 2. Accessing the panel for wiring is very difficult. Is there any way I can reset to factory settings via TIA? thanks |
| 10/6/2025 2:42 PM | |
|
Joined: 1/7/2025 Last visit: 11/5/2025 Posts: 16 Rating:
|
I have another question or solution to this problem: |
| 10/7/2025 8:28 AM | |
|
Joined: 2/10/2015 Last visit: 11/5/2025 Posts: 148 Rating:
|
You can use the SetParam block or command. Details can be found in the manual https://support.industry.siemens.com/cs/ww/en/view/109978379 |
| 10/7/2025 3:04 PM | |
|
Joined: 2/10/2015 Last visit: 11/5/2025 Posts: 148 Rating:
|
How did you validate the antenna power change? A permanent change needs to be done in the WBM of the reader. |
| 10/24/2025 6:43 AM | |
|
Joined: 1/7/2025 Last visit: 11/5/2025 Posts: 16 Rating:
|
Thanks sinec pni solved my problem and brought back wbm |