(0)| 10/26/2025 2:02 PM | |
|
Joined: 12/19/2019 Last visit: 10/26/2025 Posts: 476 Rating:
|
Here you have two options to choose from. It would be interesting to know which version you prefer. Regards, Quirin AttachmentOFF AUTO MANUAL.zip (2 Downloads) |
This contribution was helpful to
|
|
| 10/26/2025 4:29 PM | |
|
Joined: 6/11/2019 Last visit: 10/26/2025 Posts: 2652 Rating:
|
Hello Qurin, Your suggestions are well-intentioned, but if a wire breaks at the switch during operation, you won't be able to shut it down. I've also thought of something that takes wire-break safety into account and shuts down the system in the event of an interruption. But I personally consider this a very poor solution, too, since the operator may not be immediately aware of the switching mode, and the system will start up with a delay after the time set in B005 has elapsed. This could lead to misinterpretations or even accidents. Regards Ella_68 AttachmentProgrammplan-Auto-Manual.zip (3 Downloads) |
This contribution was helpful to
|
|
Follow us on