(0)| 10/28/2025 4:58 PM | |
|
Joined: 12/19/2019 Last visit: 11/6/2025 Posts: 483 Rating:
|
Try it this way. Please observe the safety instructions. Regards, Quirin AttachmentChanging Direction.zip (8 Downloads) |
This contribution was helpful to
|
|
| 11/1/2025 2:14 PM | |
|
Joined: 10/27/2025 Last visit: 11/2/2025 Posts: 4 Rating:
|
Can you send it again as an v8.1 version? I can't open it now. |
| 11/1/2025 6:56 PM | |
|
Joined: 12/19/2019 Last visit: 11/6/2025 Posts: 483 Rating:
|
Here is the version for LSC 8 Standard. I have provided NC limit switches. If using NO limit switches, simply remove the negation at the R/S inputs of the RS blocks. Regards, Quirin AttachmentChangig direction LSC 8 Standard.zip (4 Downloads) |
This contribution was helpful to
|
|
| 11/2/2025 5:36 PM | |
|
Joined: 12/19/2019 Last visit: 11/6/2025 Posts: 483 Rating:
|
If you only want to use one input for the direction change on the Danfoss VLT, you still need two outputs on the LOGO. This becomes clear when you look at version 2 in the attachment.
AttachmentChanging Direktiion LSC 8 Standard V2.zip (1 Downloads) |
Follow us on