Hello decian_mcbride145, do you see any output of the device? Your IOT2050 Advanced FS:09 comes with pre-installed IndOS in first boot order. STAT LED is not used in IndOS - only in our Example Image. You can try to skip the emmc as boot device + change boot order in Example Image or you can change the boot order in u-boot shell (serial connection required) before. BR |