(0)| 12/30/2025 2:14 PM | |
Joined: 9/27/2006 Last visit: 1/12/2026 Posts: 12480 Rating:
Hello ETN; From the Siemens FAQ 7KM: Difference between cosine phi and the power factor: https://support.industry.siemens.com/cs/ca/en/view/51402748 The PAC3220 only provides the power factor (for each phase), you can calculate the Cos PHI with this equation shown in the attachment below: In the appendix of this PAC 3220 manual, you will find the Modbus registers of your unit, and find the address of the power factor (per phase, total, max, min...) but not the cos PHI. You can use the registes for Apparent and Active (effective) power to calculate the cos PHI if you need it. https://support.industry.siemens.com/cs/ca/en/view/109767307/180448729867 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 12/30/2025 14:15:00Last edited by: dchartier at: 01/01/2026 14:59:03 |