Hello, this might help you further. I can send you the UGF password via a private message. Test the example to see if it is suitable for your task.AttachmentExample.zip (7 Downloads) |
This contribution was helpful to
|
|
| 1/30/2026 10:31 AM | |
|
Joined: 4/12/2025 Last visit: 1/31/2026 Posts: 5 Rating:
|
Hello Quirin This is what i'm looking for… I try to test it under simulation mode and seem working Still not understand your i1-i2 limits how to use, becaus the valve 3pt dont have the limit point wires… how to use your limiters? Thanks https://www.sauter-controls.com/wp-content/uploads/ImportPDM/1072032.pdf |
| 1/31/2026 12:29 PM | |
|
Joined: 12/19/2019 Last visit: 2/2/2026 Posts: 506 Rating:
|
Procedure when the actuator has internal limit switches that are not externally accessible. To maintain good control results, the time setting on the three-point step adapter must exactly match the actuator's travel time from 0 to 100%. Since the three-point step adapter stops when it reaches 0 or 100%, and the actuator's travel is also limited by the limiters, the control stabilizes within a reasonable time. Regards, Quirin AttachmentExample 2.zip (4 Downloads) |