Hi, we already discussed this in your previous post. (https://www.automation.siemens.com/tf/WW/en/Posts/40416#top) Yes, of course you can set a limit in the Drive, but the value you send from the HMI if you don't check the user entry can be anything, so it is a far more elegant solution to limit the user input at the HMI (from 0-100%), this way, no-one can send out of range values. Change the HMI/PLC to match the limit you set in the drive. Graeme
|