Hello chiawc I have a few questions for you: 1.) Did you download Netpro into both PLC's? 2.) What error/status information are you getting from you AG_SEND and AG_RECV Blocks? have alook too at the links below, perhaps they'llhelp you: Simatic Net Quick start example for Send/Receive How do you program the communication blocks FC5 and FC6? |
Cheers |
|
8/20/2010 4:15 AM | |
Joined: 1/25/2010 Last visit: 3/15/2024 Posts: 10 Rating: (1) |
1.) Yes. I did. 2.) I have tried the example for Send/Receive, but I still get the error. Please refer to the attachment for the error. Note: I am using PLCsim V5.4+SP3 to do the simulation |
8/20/2010 4:56 AM | |
Joined: 10/7/2005 Last visit: 6/8/2024 Posts: 3008 Rating: (1051)
|
That explains the problem you are having, PLCSIM does NOT (yet) support AG_SEND/AG_RECV based comms, so'll you need to test thiswith real PLC's. For completeness, how to simulate comms with PLCSIM and what type of comms are supported can be foundHERE. |
Cheers |
|
This contribution was helpful to1 thankful Users |
8/20/2010 5:50 AM | |
Joined: 1/25/2010 Last visit: 3/15/2024 Posts: 10 Rating: (1) |
Noted. |
9/24/2010 4:10 PM | |
Joined: 11/3/2006 Last visit: 8/17/2022 Posts: 7 Rating: (0) |
Darius thanks for the useful info, I also tried to make an S7 connection with CP-343-Leans..... |