Marsel, Cimplicity & WinCC are totally different SCADA programs, so you can not convert Cimplicity "device points" to WinCC Tags. You have to create a list of all I/O from your Cimplicity project, for example with "clie export" (see your Cimplicity documentation), this will create a list of all Cimplicity points and their PLC addresses. Based on that list, you can start to create WinCC tags. |
Last edited by: SteBo at: 3/28/2011 10:38 AMB r g d s , |
|
3/29/2011 5:07 PM | |
Posts: 799 Rating: (42)
|
Sorry, but I think there is no ***ibility. regards |
3/30/2011 8:57 AM | |
Joined: 10/3/2010 Last visit: 4/25/2024 Posts: 1552 Rating: (188) |
Marsel, I think you should check how the communication with S7 is done in your Cimplicity project. Depending on this, you should find the manual of this communication type which explains the addressing formats used in Cimplicity related to S7 addressing. |
B r g d s , |
|
This contribution was helpful to1 thankful Users |
3/30/2011 9:14 AM | |
Posts: 6 Rating: (0) |
Dear SteBo Thank you, for the support Best Regards Marsel |