4/12/2011 9:08 AM | |
Posts: 65 Rating: (1) |
Hi , This is Raghu. I was doing project with Analog Input module 6ES7 331-7KF02-2AB0. Am using thermocouple to measure temperature to control the heater and have to show the values in HMI. I selected measuring type as TC-I in the hardware configuration. L # IN0 ITD DTR T # TEMP4 L # IN2 L # IN1 -R L 1.200000e+004 /R L # TEMP4 *R T # OUT3 This is the Scaling program i wrote to scale the PIW Values and i have attached the Caliberation values that was calculated from the external caliberator. Could you please tell how to get linear scaling values in HMI. Advance Thanks and Regards, Raghu Splitted from SM-331 THERMOCOUPLE WITH INTERNAL COMPENSATION. AttachmentTemp Calibration_K-Type_.pdf (89 Downloads) |
Last edited by: O_Moderator at: 4/12/2011 10:56 AMnew subject after splitting |
|
4/13/2011 9:44 AM | |
Posts: 65 Rating: (1) |
Hello Aret, Thanks for your quick reply. I ill check this out and let you know shortly. Thanks again. |
4/14/2011 5:48 PM | |
Posts: 65 Rating: (1) |
Hi, Thanks for the kind reply. I think your code will help me. I will check it out and let you know soon. Thanks and Regards, Raghu |
4/15/2011 5:17 AM | |
Posts: 65 Rating: (1) |
Hi Again, Can you please tell about "OGR" and "UGR". |