Dear Mohamed, according to the rating of the motor you can connect to the drive. about the parameters , first the key parameter (p51) should set to 20 so you can change all parameters . second ; set parameter P71 (ratio between motor armature current and armature current of the drive). set parameter P76 ( ratio between field motor current and drive field current) for example : if the motor armature current is 10A and the drive current is 15A so P71=10/15 % = 67% field is the same for any clarification you can follow the attachment best regards ELSAYED ABDALLAH AttachmentMicrosoft Word - 6RA22.pdf (289 Downloads) |