Hello Artem Khodos you can achieve event driven (PLC initiated and cycle precise)message generation via usage of the various Alarm_S and/or Alarm_D and/or Alarm_8 blocks . Which ones to use depends on the type of CPU that you useand you'd need a Siemens HMI/SCADA system as the counterpart. As an alternative,P-Diag in combination withProAgent may be considered too (this is however and optional and chargeable extra, but will save youa fair bit of "manual" programming effort). Below is one example link to get you started and which should help you todetermine if that is what you after (you'll find more with the inbuilt help on the Alarm_S/D/8 blocks and with asearch for them @ https://support.automation.siemens.com): How do you display ALARM_S or ALARM_D messages with process values (so-called associated values) on a WinCC flexible operator panel? I hope this helps |