Hello RamenshK; To my knowledge there are no HART modules dor the S7-400. You would need to use an ET 200M Profibus-DP slave station with S7-300 HART analog input and output modules. You would need PDM v. 6.0 and a HART modem to configure the HART field devices. Your program would include READ_REC and WRITE_REC functions (SFC 58/59) to collect the HART data from the HART inputs and to write HART data to the HART outputs.You can get an overview of the requirements in the following manual: SIMATIC ET 200M distributed I/O device HART analog modules 3.2.1 Configuring the HART analog module and field devices Overview You configure the HART analog modules ● In the SIMATIC S7 system with STEP 7 as of V5.4, SP3 and in the HSP 0119 V2.0 for the module "AI/AO 8x16 Bit HART, V3.x". ● Using the current GSD file of the IM153-2BA02-0XB0. You calibrate the HART analog modules ● Using SIMATIC PDM V6.0, SP3 + HF2, see Chapter Calibration (Page 89). You parameterize the field devices ● With SIMATIC PDM V 6.0 Service Pack 3 or higher and the EDD for ET 200M modules V 1.1.8 or higher. If you have configured the module as of V3.x, you need the EDD for ET 200M modules as of V1.1.10. You use the HART-Fast-Mode ● With SIMATIC PDM as of V6.0 + SP5. Hope this helps, Daniel Chartier |