3/14/2013 5:29 AM | |
Posts: 15 Rating:
Dears can anybody will suggest me if......... i am going to design 412-5H system with UR2-H rack. As in UR2H Rack IO bus and communicaiton Bus are electrically isolated . i) where would i install the IO modules? ii) if i install all the IO modules with CPU in Rack0 and if the Rack0 CPU fails, will the modules will still be accessable by Rack1 CPU? Please also find my Design in the attachment. Regards Shahid AttachmentDesign Clarification.pdf (258 Downloads) |
3/20/2013 7:26 AM | |
Posts: 15 Rating:
Thanks a lot for your reply dear Will you please give your valuable comment about my design. Am i on the right trak? Best Regards Shahid AttachmentDesign Clarification.pdf (229 Downloads) |
3/21/2013 7:03 AM | |
Posts: 515 Rating:
Hi sraza, Kindly find attached a sytem configuration using s7 400 412-5H. I hope this would be helpfull to you.
AttachmentS7 400 412-5H SA.pdf (380 Downloads) |