Hello. 2Q - 6RA8025-6DS22-0AA0 4Q - 6RA8013-6DV62-0AA0.
|
7/1/2013 4:32 PM | |
Posts: 378 Rating: (73) |
Dear KSN, Thanks for replay I have doubt since my motor is permanent magnet i dont have a place to connect the field output so if i connect armature supply and left the field output I guess i will have Field loss alarm with no operation. Is there any possiblity to disable field output? Regards |
7/1/2013 5:14 PM | |
Joined: 8/25/2006 Last visit: 11/17/2024 Posts: 2211 Rating: (280) |
Yes, you can disablefieldviaparameter. |