6/2/2012 2:35 PM | |
Posts: 12 Rating: (0) |
Good Day, On how to determine the interrupting capacity of the breaker you should cumpute the Isc your network...there is a lot of computation needed to know in interrupting capacity(KAIC). here is the attached file hope that can help you...if you have question and feedback im open to help.... AttachmentCalculation of short-circuit currents.pdf (582 Downloads) |
This contribution was helpful to5 thankful Users |
7/2/2013 7:25 AM | |
Joined: 7/8/2009 Last visit: 8/5/2024 Posts: 1976 Rating: (477) |
Hello Deep I was searching from google and found some nice explanation http://mandrelectrical.com.au/karatings.php http://www.electrical-installation.org/enwiki/Selection_of_a_circuit-breaker I think, this will guide you further Hope this will help you Best Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
This contribution was helpful to4 thankful Users |
7/2/2013 7:46 AM | |
Posts: 262 Rating: (45) |
Hi, In Siemens, we recommend to use the best way of calculating Fault level and that is SIMARIS Software... please refer the below link and download it freely and use extensively... https://www.automation.siemens.com/mcms/electrical-design-software/en/service-support/simaris-software/Pages/default.aspx |
7/17/2013 1:48 PM | |
Posts: 202 Rating: (16) |
Hi There Can any tell me how the Fault level for transformer is decided as from that fault level the PCC & MCC panel are designed ???