What this error code means. Have anybody faced this issue while S7 loading. Result of this error make one S7 in stop mode. |
2/18/2013 3:54 PM | |
Posts: 5 Rating: (0) |
yes i did some hardware changes, added new FUM cards. and while hardware loading this error happens. |
2/19/2013 1:25 PM | |
Joined: 1/3/2006 Last visit: 2/19/2024 Posts: 726 Rating: (71) |
From Step 7 help [img]/tf/WW/en/postattachments/download?attachmentId=34581&onlyInternet=False[/img]
|
2/19/2013 2:16 PM | |
Posts: 5 Rating: (0) |
Thanks for the attachment, means error happened while configuring the connections. |
2/19/2013 2:22 PM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
Yes, give us details about your changes and the type of hardware used there. Best regards, Hristo Mihalev
|
5/8/2013 1:22 PM | |
Posts: 5 Rating: (0) |
System was upgraded from simatic version 5.4 to 5.5. |
8/26/2013 7:14 AM | |
Posts: 15 Rating: (1) |
I am facing the same problem. Event ID 16#43DC Parameter reassignment of slots not permitterd. (Only adding or removing allowed) Station No: 33 DP master system ID: 3 all time Rack0 (master) running normally and Rack1 got in to stop mode. Please provide solution. |
Last edited by: HITUL007 at: 8/26/2013 7:17 AMAlso have SFB 20 STOP event is there. |
|
8/26/2013 7:28 AM | |
Joined: 7/9/2013 Last visit: 11/10/2020 Posts: 2 Rating: (0) |
Hello, The problem which you are facing is because you are reconfiguring the hardware changes, as only adding or removing allowed, Means if you are configuring a new hardware on the same slot where an old hardware exist . -first you have to remove the old hardware, load the s7 ->then add the new hardware and again load the s7. |
8/27/2013 6:26 AM | |
Posts: 15 Rating: (1) |
Thanks for the solution... I have deleted all the devices on that segment & download than again reconfigured all devices and problem solved.... thanks again... |