The ring closes via the FO based redudancy link between the two CPU's, see System Redundancy with IM153-4 PN IO High Featurefor more on this.
You are actually NOT using "traditional' Profinet MRP in this case, but afeature that Siemens (arguably misleadingly) calls "System Redundancy". While I can't offer any hands onexperience with this just yet, you'll see from the previous link thatthe changeover time will be "typically" about30ms (and better be bumpless withoutI/O time out). Have a look too at chapter 8 of the SIMATIC Fault-tolerant systems S7-400H for more on the subject of using Profinet I/O's in a H-system. I hope this helps |