No these FBs are for ptp CPU onboard port. You HAVE to buy the modbus license from Siemens. |
9/27/2014 5:23 PM | |
Joined: 9/27/2006 Last visit: 6/14/2024 Posts: 12260 Rating:
|
Hello Vithani; In the MM440, the parameter for USS node address is P 2011, and its value must be 0-31. See this Tips and Tricks project diocumentation for the S7-200 USS protocol with a MM420: 2,5 Parameters for the MM420 ... //P0700=5 Set local/remote control mode by setting //P1000=5 Set local/remote control mode by setting //P2010 Index 0 Value 7 (19200) Baud rate //P2011 Index 0 Address 1 (0 to 31) Slave address //P1120= 0.00 (0 to 650.00) Acceleration ramp //P1121= 0.00 (0.00 to 650.00) Deceleration ramp // // Set the serial link timeout by setting: //P2014 Index 0 Value 300 (0 to 65535 ms) // Value 0 is without monitoring // When you change this value, the PLC must already carry out the // USS protocol, as otherwise Error 72 is immediately reported. // You must also change the value with the arrow pointing down, // as the first value would be 1 ms if the arrow were pointing up, resulting // in the immediate reporting of an error. ,,, Attached you will find a pdf version of the complete Tip documentation. Hope this helps, Daniel Chartier AttachmentTIP 65 Position control over USS.pdf (289 Downloads) |
9/27/2014 5:25 PM | |
Joined: 9/27/2006 Last visit: 6/14/2024 Posts: 12260 Rating:
|
Hello again Vithani; Maybe this document provided by Late in an old thread, could help you out with the details of the USS protocol: point to point CP340 RS485 communication with MicroMaster MM25/2 Hope this helps, Daniel Chartier |