Industry Online Support
Technical Forum
8/12/2014 7:11 PM | |
Joined: 1/15/2009 Last visit: 4/19/2024 Posts: 316 Rating: (40)
|
Problem number 1: I would check the scaling of the blocks in CFC (both the drive block and Motor block if you are controlling it that way). Check all the scales, inputs, outputs, readbacks, and verify this match with what you would expect. Problem number 2: Not so sure, perhaps this may be as the same as number 1. Maybe the scaling is off a bit. More information on Drive ES for PCS 7 can be found herehttp://support.automation.siemens.com/WW/view/en/58007228
|
The best location for all PCS 7 content (manuals, guides, application notes, FAQs, and videos). |
|
This contribution was helpful to1 thankful Users |
8/14/2014 9:44 AM | |
Posts: 31 Rating: (1) |
Hello, Thank you very much for support. I would check and confirm. Regards, Krunal Shah |
Last edited by: Krunal Shah at: 8/14/2014 9:45 AM |
|