7/8/2015 3:17 PM | |
Joined: 6/13/2012 Last visit: 10/19/2022 Posts: 161 Rating: (4) |
Hello! I was looking for the information about Simultaneously active Alarms in 6ES7414-4HM14-0AB0, and got this manual: A5E00267695-09 But there is strange information about it. Simultaneously active Alarm_S/SQ blocks or Alarm_D/DQ blocks = max 100, like CPU 412–3H,and almost like s7-315. Is it erratum or not? I think amount could be more than 100. Thanks. |
7/10/2015 7:15 PM | |
Joined: 11/29/2011 Last visit: 10/24/2024 Posts: 1360 Rating: (232) |
Hi, If you see the link below, you may notice that with S7-400 you have
"ALARM_8" block listed as well. This option expand the number of active
alarms. The article detail a 416-3, but you can use the same table to look up your CPU. Look at this: What should you watch out for when using the alarm numbering procedure? In this article you can read: "Example taking CPU 416-3 to better explain the maximum values given in Tables 4 and 5:
|
Last edited by: MicroMan at: 7/11/2015 12:54:59 AMAdded details - What you read here, please check with manuals and your requirements. |
|