Can anyone lend a hand converting the attached from a Mitsubishi PLC to Siemens LAD Logic please? We need to remove the Mitsubishi PLC and add this code to our Main Siemens PLC. Thanks. AttachmentELTFLAG.pdf (107 Downloads) |
11/4/2015 2:52 PM | |
Posts: 366 Rating: (30) |
Hello, look at the attachment. One very important difference between Mitsubishi and Siemens is the addressing. On Siemens side it works bit-wise like "I0.0, I0.1, I0.2... I0.7" = InputByte 0 and "I1.0, I1.1, I1.2... I1.7" = InputByte 1. In Mitsubishi side its all hexadecimal like "X000,X001,X002...X007" = Inputbyte 0 and "X008, X009, X00A ... X00F" = InputByte 1. Inputs on Siemens "I" on Mitsubishi "X" Outputs on Siemens "Q" on Mitsubishi "Y" Marker are the same Timer are the same nice regards AttachmentFC1.pdf (111 Downloads) |