Hello, In 18month every relay have 580kcicles. as you can see in technical data max (teoric) number of operation for relay is 100kcicle at rated voltage . also considering 10Mcicle (mechanical limit) you hare near the end of relay life. Also switching frequency is out of max (1Hz that means 0,5sec on and 0,5s off). In my opinion you have to use plc with electronic digital output (if you like s7-200 there is 214-2AD23) and solid state relay. P.S. actually do you have parallel diode in relay coils??? Best Regards
|
★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★★ |
|
11/10/2015 10:39 PM | |
Posts: 21 Rating: (0) |
No Sir, no any diode with the parallel of relay coil. |