Hello Idir, We're getting there... OK, you have a real motor. and so you have a real input as well?? Is I2.0 the feedback run of the motor? Or is it a signal to start the motor? I was thinking the input was the feedback run and so you don't use it to start the motor....Apparently, it is a start signal for the motor. Correct? I think you mean PV_Out of the OutStart block? In that case, you have it correct.. The signal: Start from the motor block is meant to start the motor by activating a digital output. When you have your feedback run signal (FbkRun=1), then the signal Run is set to "1" as well as FbkRunOut of the motor block. And RdyToStart is used to indicate the motor can be set to run in automatic mode. You can use that signal in a SFC or so to check if all equipment is ready to go.. It is made up of the following conditions: - No group error - No interlock active - No forced operating mode or manipulated value - No rapid stop - Block is in automatic mode - Restart waiting time has expired |
If I could help you, you can use the RATE button. Thank you. |
|
12/26/2015 2:43 PM | |
Posts: 163 Rating: (2) |
Hello, I would like to use both of them the distributed I/O and Ethernet. Also I have an off-tpoic question. [snip] ... Regards, ------------ new question splitted to: Simatic Thin Client and Simatic Multi Panel. Which one will be my OS? |