1/22/2016 4:53 PM | |
Posts: 439 Rating: (109) |
Hello Lukask, AS-i master can handle up to 62 AS-i slaves as describe in the manual page 15. Here it is: Manual CM AS-i Master for SIMATIC ET 200SP Best regards, Hugo |
Last edited by: HugoD at: 1/22/2016 4:54:26 PM |
|
1/22/2016 5:25 PM | |
Posts: 19 Rating: (0) |
Hello Hugo, Thanks for Yours reply. I found this in manual: Connection to power busbars PAGE 27 in this manual My slaves takes power supply from AS-i bus. There are 35 slaves with current 90mA and 7 with 180mA. And it gives about 4,4 A. I want to use 8 A power supply but I see that this master permits maximum 4 A ? |
Last edited by: ld22 at: 1/22/2016 5:25:57 PM |
|