8/29/2005 3:42 PM | |
Joined: 8/10/2005 Last visit: 4/9/2024 Posts: 1486 Rating: (32)
|
in principle there are 2 ways to recognize running ET200M nodes: 1. Read back a flashing output by an Input (wired to the output) 2. Using SIMATIC Diagnostic features Using diagnostic features is in my opinion the best way. There are documented Diagnostics Blocks for PROFIBUS DP (FB125, FC125) for free download http://support.automation.siemens.com/WW/view/en/387257 There is a documented PROFIBUS Diagnostics Package for SIMATIC S7 and TD/OP (for free download) if you would like to show errors on panels. http://support.automation.siemens.com/WW/view/en/5362473 |
Last edited by: CS Moderator at: 10/12/2005 1:42 PM |
|