Hi, Looks like you have AS RT PO License error. CPU-410 5H is preloaded with 100 AS RT PO licenses, you will have to upgrade the same. Check links below for more information PCS 7 Licenses and configuration limits (V8.1 SP1): Page12 shows Levels for AS RT PO License: How are the licenses for the AS and OS counted in PCS 7 V7.0 onwards? |
3/14/2016 8:27 AM | |
Posts: 70 Rating: (0) |
Thank you so much PSW Can you show me how i update license for my CPU ? need to contact siemens or any download for it ? once again, Thanks You. |
3/14/2016 9:19 AM | |
Posts: 129 Rating: (17) |
Hi, AS RT PO License is upgraded thru System Expansion card (MMC) loaded on backside of CPU-4105H. Check from page 55 of manual from link below: |
3/14/2016 11:02 AM | |
Joined: 3/14/2008 Last visit: 9/27/2024 Posts: 2098 Rating: (938) |
Hello MD_dx, There is a procedure in order to update your PO. Luckily, you can update all at once, instead of doing this per 100 for example. Some collected info on how to work with the procedure: 1.Order the additional PO at your Siemens contact person or online through the Industry Mall, PO's are available at 100 or 500 PO. If you need 300, you can order 3x100 PO. Please note, when using a H-system, you have to have the PO distribute symmetrically: 300x AS1 and 300x AS2.The volume of the expansion pack cannot be distributed to different CPU's (or SEC's). 2. Create the PO activation file using Simatic Automation License Manager-> Select Edit->Connect Target System-> Connect AS410 and connect to your desired CPU. Drag the license keys for the CPU410 expansion packs and drop them to the automation system. Open the online folder and select the license key-> License->Upgrade. 3. Send the PO activation file via Support Request (you can create one request for all your PO activation files). In the folder: Siemens->Automation->PCS7->Activations is the PO activation file located. Open a support request at http://www.siemens.com/automation/support-request and fill in necessary info. 4. Receive the PO release file and transfer it to the SEC of the CPU using the ALM. Connect to target system, drag the PO release file and drop it to the online folder of the CPU. |
Last edited by: Oreca at: 3/14/2016 11:10:18 AMIf I could help you, you can use the RATE button. Thank you. |
|
3/14/2016 11:17 AM | |
Posts: 567 Rating: (107) |
Hello MD_dx, there is an application example availble which describe the PO-upgrade for S7 410-5H. The application example "Process Automation with the SIMATIC PCS 7 CPU 410-5H Controller" you can find under the following link: https://support.industry.siemens.com/cs/ww/en/view/96839331 The Information about the PO-upgrade you can find in chapter 2.5 |
3/15/2016 3:22 AM | |
Posts: 70 Rating: (0) |
Thank you all |
4/7/2016 9:38 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by MD_dx is split to a separate thread with the subject my CPU is grey out in ALM. Best regards |