hi lakbodom, first, I think this manual can help you to understand: SIMATIC Distributed I/O System Fail-Safe Engineering ET 200S Distributed I/O Systemhere the answer on your questions: 1) Chapter 3.1 and 7.5: channel 0, pin1 E0.0 channel 1+5 pin 2+10 channel 2 pin3 E0.2 channel 3 pin7 E0.3 channel 4 pin9 E0.4 channel 6 pin11 E0.6 channel 7 pin15 E0.7 which VS you need depends on the parameter settings of the module. Have a look in chapter 7.5.5 2) yes there is a table, that can help you: S7 Distributed Safety V5.4 and V5.4 + SP 1,2,3,4,5: Product Information on F Execution Times and F Monitoring and Response Times3) the size of the process-image doesn´t limit the usable adresses. process image of the inputs will be updated before OB1-cycle and the process-image of the outputs will be written after OB1cycle. The adresses in the process-image can be accessed with eg. I0.1.x, IB100, IW200, ID52,Q0.2, QB20,QW54,QD80. Adresses that are inside the process-image can be accessed with perpherial accesses, like, eg. PIB348, PIW256, PID656, or PQB222, PQW412, PQD512. Bit-access is not possible. In TIA the periperial access is with, eg, IW234:P failsafe input adresses are read in before safty program, and the output adresses are written after execution of fail-safe-programm. more about that in this manual, chapter 5. SIMATIC Industrial Software S7 Distributed Safety - configuring and programminghope this helps, regards, |