4/19/2016 9:18 PM | |
Posts: 7 Rating: (0) |
I have a redundant System which is shown in picture# 3. When i assigned IPs to my redundant CPUs then Maintenance Fault occured.It says IP conflict on the network but i dont have anything on this network other than this AS. I have also tried by changing the IPs but this fault does not disappear. Please help me if anybody know how to remove this fault from the CPU. AttachmentPics.zip (84 Downloads) |
4/20/2016 7:54 PM | |
Joined: 9/7/2007 Last visit: 10/9/2024 Posts: 550 Rating: (62) |
Hi M_Sohaib I checked your attachment and found that you have CP443-1. Can you try to disable the ports of the CPU and use the CP443-1 to establish communication. |
Best Regards |
|
4/21/2016 8:35 AM | |
Joined: 3/14/2008 Last visit: 11/9/2024 Posts: 2124 Rating: (951) |
In a redundant fault tolerant plant bus, you always must assign the IP addresses in a different range. For example: Ring 1: 192.168.1.0-192.168.1.255, Subnet: 255.255.255.0 Ring 2: 192.168.2.0-192.168.2.255, Subnet: 255.255.255.0 Maybe this could be your problem..... |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to3 thankful Users |
4/21/2016 8:55 PM | |
Posts: 7 Rating: (0) |
@Oreca You are right. This has solved my problem. Thanks for your help. |