Hi Alex, as you have read the manual about fault tolerant process control you know that are two ways to set up a redundant terminal bus. 1) Intel-Teaming mode; as the name says this is only possible with specific Intel Ethernet adapters 2) Parallel redundancy protocol (PRP). For that you need the Industrial Ethernet SOFTNET-IE RNA software package (and for sure the license). This should be working with other than Intel adapters, too. But there is a wide variety of adapters available so that not all can be tested by Siemens. Just read the manual and see the requirements there. Regards |