Hello Sadiq; First, you cannot force a value in a DB with Step 7. See the attachment, taken from the Programming with Step 7 manual. You can modify it qwth a VAT table, for example. https://support.industry.siemens.com/cs/fr/en/view/18652056 Next: I do not see how you want to control the state of your valve with an input. You have a pneumatic valve, connected to an AS-i input signal. This input tell the AS-i master the status of the valve (open/closed). If you want to send a command to the valve, you should have an output to control it, and the adequate circuitry. Hope this helps, Daniel Chartier |
This contribution was helpful to2 thankful Users |
9/18/2016 9:42 PM | |
Joined: 1/21/2016 Last visit: 4/22/2023 Posts: 83 Rating: (1) |
is a pneumatic valve input ? is not asi saved as i and Q ? |