Joined: 7/9/2015 Last visit: 10/14/2024 Posts: 3969 Rating: (591) |
Hi, please check the following manual: SIMATIC Distributed I/O System Fail-Safe Engineering ET 200S Distributed I/O SystemIn chapter 5 Diagnostics you will find information about Fail-safe vaule output (Page 54) and F-module with inputs (Page 55). i.E. for INPUTS you can read: If a communication error is detected, the current process values remain set at the inputs of the F module and the channels are not passivated. The current process values are sent to the F-CPU and are passivated in the F-CPU. Regards, Towome |
|
|
2/21/2017 9:40 AM | |
Joined: 10/26/2015 Last visit: 10/12/2024 Posts: 20 Rating: (1) |
thanks Towome but i wanna know what happened when profibus cable break ?? my emergency output goes 1 or 0 ?? |
2/21/2017 10:03 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi calyon, the ET200s modules give the safe value 0. see the manual already provided, chapter 5.1
In other F-modules you have other possibilities, like ET200M. in properties of the module you can set what the module should do. you can say: -use substitute value 0 -keep last valid value SIMATIC Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modules in chapter 6.1.3 you see how to handle this.
hope this helps, regards, |