Joined: 3/19/2015 Last visit: 1/10/2022 Posts: 30 Rating: (1) |
I have researched a bit and asked siemens support and they gave me a solution a DP/PA has a IM, one or more DP/PA coupler (see the following web: https://support.industry.siemens.com/cs/es/es/view/51678187 ). To configure in tia portal is making a custom GSD. Look at the following link. https://support.industry.siemens.com/cs/es/es/view/79159361 The custom GSD must have the reference you want and the DP/PA coupler and the PA instruments. To install the custom GSD, see the following link Regards
|