5/19/2008 2:59 AM | |
Posts: 7 Rating:
The manual shows redundant 24V DC power from network 1 and network 2. Will the coupler operate properly if 24V DC from only one network is supplied? |
5/19/2008 5:04 PM | |
Posts: 5822 Rating:
Hello, I would say if you bridge the power from DC1 to DC2 than it should work still. I see no reason why it should not work. Best regards J_Bell |
5/22/2008 8:04 PM | |
Posts: 7 Rating:
Thank you. One additional question: what would be the current rating for a 24V supply to the couplert? I just can't find it in the 6ES7 158-0AD01-0XA0 specs. |
5/22/2008 11:52 PM | |
Posts: 5822 Rating:
Hello, in the technical specs of the Coupler about 90 mA are mentioned See DP/DP CouplerApendix A 2 Best regards J_Bell |