4/16/2017 9:04 PM | |
Posts: 20 Rating: (0) |
I am going to install a Siemens PLC on a project. It has relay outputs and I am in two minds whether I should slave the outputs through relays before driving contactors like ABB's A-Lines or just directly connect. I've heard if the output from the PLC is going to a "high load" device like a motor operated valve or a motor starter I should always use a interposing relay no matter what kind of output I have on the PLC. Little things like pilot lights and outputs for permissive to other devices (voltage sense inputs) it would be OK wiring direct. Is that accurate? Your thoughts would be appreciated. |
4/16/2017 9:14 PM | |
Joined: 12/18/2014 Last visit: 10/14/2024 Posts: 33954 Rating: (4221)
|
You post in the LOGO! conference. Did you mean with Siemens PLC a LOGO! ? Or mean you a S7? |
4/17/2017 2:34 PM | |
Joined: 11/14/2016 Last visit: 3/5/2024 Posts: 218 Rating: (3) |
Hi your thoughts are absolutely accurate. A coupling relay costs very little money but can save your PLC. |