Hi Cammo, Yes, you are correct. Changing a setpoint is not allowed in local mode. The only thing you can do is change setpoint internal/external if localsetting is set to "3" or "4". You have to create some logic to influence external setpoint when local mode is active. Like using a analog input signal from your local panel, with a switching logic (like an analog value selector block before connecting to SP_Ext: SelA02In). |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
6/15/2017 7:50 AM | |
Joined: 3/22/2016 Last visit: 2/21/2024 Posts: 5 Rating: (0) |
Thanks Oreca, I had thought as much. You just never know sometimes. |
6/23/2017 4:02 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (928)
|
Hi cammo, I have some very good news for you. I came across a new update for PCS7 v8.2: AP library v8.2 SP2 With SP2 it is now possible to change the setpoint in local mode: Quote from readme:
You can download the service pack from here: PCS7 V8.2 AP library SP2 download PS: If you have updated the blocks and faceplates, make sure you set your MotSpdCL Feature2.bit6 to "1" because only then the operator is allowed to change the speed in local mode. Good luck! and enjoy the possibility of changing the setpoint in local mode! |
Last edited by: Oreca at: 6/23/2017 4:04:50 PMLast edited by: Oreca at: 6/23/2017 8:56:35 PMIf I could help you, you can use the RATE button. Thank you. |
|