Is it 1AC 230V FSA one? If so it might be insufficient voltage in control circuit for example - I've run across few of those in the early V20s. I understand you have formed the capacitors before powering it up? First try to clean the PCBs etc. with compressed air if it was in storage for so long. If the fault is still present you could try to add power from external source to 10V or 24V terminals (check the level first) - this one applies if it's 1AC 230V FSA one from early batches. And the last but not least, fixer of most red LED issues - firmware upgrade. |
Last edited by: m_zlotek at: 1/2/2017 7:27:07 AMLast edited by: m_zlotek at: 1/2/2017 7:28:01 AMLast edited by: m_zlotek at: 1/2/2017 9:44:55 AM |
|
6/15/2017 5:13 PM | |
Joined: 4/29/2007 Last visit: 11/5/2024 Posts: 11 Rating: (0) |
Hello, I have a same problem with Sinamics V20 400V FSC . Need Formed capacitors too. Can I try to add power from 24V terminal? thanks
|
6/19/2017 10:59 AM | |
Joined: 3/31/2015 Last visit: 11/5/2024 Posts: 175 Rating: (16) |
Did you try upgrading the firmware? Usually does the trick. |