Hi! My little addition:An Emergency Stop is a fail-safe control switch or circuit that, when de-energized, will stop the operation of associated equipment and will shut off all potential hazards outside the main power enclosure. An overview of the European standards applicable to Emergency Stops: ISO 13850 / 4.4.4 Gives requirements for the emergency stop function of a machine, whatever the energy used may be:
EN418 / 4.1.11 Gives requirements for the emergency stop function of a machine In addition to the ISO 13850 requirements above, EN418 more specifically states:
IEC 60947-1 Low Voltage Switchgear and Control Gear: General Rules IEC 60947-5-1 Control-Circuit Devices and Switching Elements, Electromechanical Control Circuit Devices IEC60947-5-5 Control-Circuit Devices and Switching Elements, Electrical Emergency Stop Device with Mechanical Latching Function IEC 60204-1 Gives additional requirements for an emergency stop function realized by the electrical equipment of a machine, specifically installation methods and location requirements. Andhereis a few emergency stop circuit examples (be aware, that standards mentioned that site is Australian). Hope it helps. |