Dear Sir, Please see the attachment. I want to upgrade the existing system.it is said that I will have to install 3964 R protocol.Is it to installed on computer? Or is it require to install some files on S5 PLC? Please suggest. Regards, AttachmentSCHEMATIC BOOM 1.pdf (233 Downloads) |
Last edited by: CS Moderator at: 6/24/2008 12:56 PMnew subject after splitting Last edited by: jitu at: 6/24/2008 10:38 AMLast edited by: jitu at: 6/24/2008 10:38 AM |
|
6/24/2008 2:36 PM | |
Posts: 63 Rating:
|
I think that there is simple error in attached pdf. In my opinion: ET200 stations (profibus slaves) are connected to IM308, and Lauer OP is connected to secondary port of CPU945. If you want to connect a PC with 3964R protocol you have to assign parameters for CP544 by COM PP software or make it in S5 software. You have also add calls of SEND and RECEIVE blocks in CPU. Link to CP544 documentation: http://support.automation.siemens.com/WW/view/en/1108809 |