9/15/2017 2:16 PM | |
Joined: 9/27/2006 Last visit: 7/7/2024 Posts: 12268 Rating:
Hello cemo; IEC 61511 is a standard for Functional Safety- Safety Instrumented Systems; as such for any implementation of this it will refer to F-Systems (or Distributed Safety) and F-CPUs with F-I/Os. These documents could probably provide the information you need: http://w3.siemens.com/topics/mea/en/safety-integrated/process-safety/pages/process-safety.aspx Trainings for SIMATIC PCS 7(incl. IEC 61511) Energize to Trip Requirement for SIL 3 according to IEC 61511 (Safety Manual) Wiring and Voting Architectures for failsafe Analog Input Modules (F AI) of the ET 200M The most important steps, as always with Functional Safety, is the Risk Assessment of the project and the determination of the required SIL levels to meet the conclusions of the assessment. Then you can choose to follow IEC 61511 (ISA 84) or IEC 61508 depending on the type of project you need to implement. Hope this helps, Daniel Chartier |
This contribution was helpful to
1 thankful Users |
9/15/2017 7:05 PM | |
Hello cemo; So basically you intend to develop an SIS application with a S7-400H CPU, non redundant, and without Safety CPU and I/Os, without a Safety program? One basic question, for yourself and others here interested in the question: how will you attain any certified SIL level with the architecture you propose? https://www.automation.siemens.com/w2/efiles/pcs7/pdf/76/br_safety_2014_en.pdf Hope this helps, |