5/17/2018 1:10 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi StamGuy, current measuring 2-wire and PT100-measuring are two totally different measurements. Your module 6ES7134-4GD00-0AB0 can only work with 2-wire-transducer. If you have a PT100-sensor you need to use a RTD-module, like 6ES7134-4JB51-0AB0 hope this helps, regards, |
FCK WAR! |
|
5/17/2018 2:03 PM | |
Joined: 3/20/2017 Last visit: 9/26/2024 Posts: 143 Rating: (2) |
I have a transducer with the PT100 so I get a 4-20mA signal |
5/21/2018 11:54 AM | |
Joined: 3/20/2017 Last visit: 9/26/2024 Posts: 143 Rating: (2) |
Here is the data sheet of the device
AttachmentTP100.pdf (137 Downloads) |
Follow us on