UNSCALE FC 106 In TIA 13 - S5TIME |
6/7/2018 5:26 PM | |
Posts: 2826 Rating: (684) |
The RET_VAL is feedback of an alarm code. It does not make sense to feed this into a time value. Is that time value used anywhere in your program. Just simply make that tag (variable) a WORD type. -- With "IEC CHECK" deselected in the code block attributes, a WORD can be moved into an S5TIME tag. Do realise that S5TIME is a very special coding: 4 bits unit size and 3 BCD digits. -- Further reading - Have a look at what the information system (Help inside TIA Portal software) provides on the following topics: Regards. AttachmentEvaluating errors with output parameter RET_VAL.pdf (56 Downloads) |
Last edited by: #dP at: 6/7/2018 5:30:21 PMadd PDF of what RET_VAL can mean Last edited by: #dP at: 6/7/2018 5:32:19 PM |
|