You set the time synchronization in your WinCC project under "Time Synchronization". There you select your CP1613 card to master for ALL your servers. This means that all servers will try to take the master token, but when one has taken it all the others turn to slaves. If the master disappears then the servers will try for the token again. R. http://support.automation.siemens.com/WW/view/en/15390777 |
Runis |
|
9/5/2008 5:45 PM | |
Posts: 2661 Rating: (279) |
Hi irb6, Runis is right. You do not needany settings on the CP1613 itself. You just need to set both CP1613's as masters (see attachment) in the WinCC Time Synchronization editor. The online help gives a good explanation of the various setting combinations. Regards AttachmentTimeSyncServerSettings.pdf (300 Downloads) |