6/8/2011 4:26 PM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046)
|
Hello ercag Siemens changed the firmware of the PAC's Profibus DP module some time ago to give it DPV1 capability. This does however also require usage of a new GSD file and I supspectthat this the reason for your problem. Have a look at the links below and please let us know what you find. Unable to establish a connection between SENTRON PAC3200 and S7 PLC via Profibus DP GSD files - Expansion module PAC PROFIBUS DP |
Last edited by: fritz at: 6/8/2011 4:27 PMtypos Cheers |
|
6/8/2011 4:40 PM | |
Posts: 32 Rating: (2) |
I also download the GSD file from same place.So I use GSD file SI018163.GSE date 14.10.09. |
6/9/2011 2:13 AM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046)
|
So your are using the DPV1 GSD file for the PAC which means that youMUST have the V2.0 FirmwarePAC-Profibus-DP interface module installed in it. Can you confirm this? (or do you perhaps have the older V1.0 FirmwarePAC-Profibus-DP interface module, if so you MUST use the SIEM8163.gsd file). |
Cheers |
|
6/9/2011 9:50 AM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046)
|
Hello ercag please confirm that you do have theFirmware V2.0PAC-Profibus-DP interface module installed. Have a look at chapter 6.5 of the Manual Expansion modules PAC PROFIBUS DP to see how to read it out. While there, can you also check the Diagnostics of the PAC-Profibus-DP interface module and see if it provides further clues. The only testI can think of is to try a different PAC and/or Profibus moduel for it (it may be faulty) |
Cheers |
|
6/10/2011 9:23 AM | |
Posts: 32 Rating: (2) |
Hello Fritz; Attachment I'm sending the foto of Firmware screen. Thanks; |
6/10/2011 9:50 AM | |
Joined: 10/7/2005 Last visit: 4/26/2024 Posts: 3004 Rating: (1046)
|
Hello ercag well,your picture clearly shows that your PAC Profibus module isa Firmware V3.0.2 one. What I don't knowis if it too perhaps requires a different GSD file. I presume it will requrie the same GSD file as the Firmware V2.x Profibus DP module butsuggest you send a Support Request to Siemens (see "Contact box" on the right hand side of this thread)and let us know what they advise. In the meantime, have you tried a different PACand/or Profibus DP module? |
Cheers |
|
6/10/2011 11:39 AM | |
Posts: 32 Rating: (2) |
Hi Fritz; I have 6 sets of same PAC3200 and all are connected to profibus and all has the same fault. Thank You; |
9/5/2018 1:44 PM | |
Joined: 7/31/2017 Last visit: 1/29/2024 Posts: 1 Rating: (0) |
Hello, I am having the same issue. Did you ever find a solution to this problem?? Thanks. |