Using TIA Portal to program an S7-300 PLC. I've got a byte in the private INPUT area of an FB. Is there a way to access individual bits of the byte? |
9/28/2018 9:38 PM | |
Joined: 12/4/2009 Last visit: 4/25/2024 Posts: 452 Rating: (134) |
evanmars1, perhaps you can use slice access: How in STEP 7 (TIA Portal) do you access the unstructured data types bit-by-bit Hope this helps. Regards, |
If this post actually helped, you may consider using the Rate button above. |
|
9/28/2018 9:55 PM | |
Posts: 2826 Rating: (684) |
Hello crazyCow.
A gentle reminder - slice access relates to the S7-1200 and S7-1500, while the question orbits around the S7-300.This is also the reason for stating about the option of using AT overlay in (only) SCL. BR |
Last edited by: #dP at: 9/28/2018 9:57:12 PM |
|
This contribution was helpful to1 thankful Users |
9/28/2018 9:59 PM | |
Joined: 12/4/2009 Last visit: 4/25/2024 Posts: 452 Rating: (134) |
Arhg! Somehow I missed the target controller. Thanks and regards! |